查看: 1685|回复: 1
收起左侧

[规范类] ABS OFFSHORE SUPPORT VESSEL GUIDELINE

[复制链接]
发表于 2012-6-12 23:06 | 显示全部楼层 |阅读模式 来自: 中国福建福州
ABS的离岸供应船的指南中,第5章第6节关于溢油回收船的一处要求(5-6-4/17.1.2)
17.1.2 Portable Foam Applicator Units
Two portable foam applicator units are to be provided. A portable foam applicator unit is to c***ist
of an air-foam nozzle of an inductor type capable of being connected to the fire main by a fire hose
together with a portable tank containing at least 20 liters (5 U.S. gall***) of foam-making liquid.
The nozzle is to be capable of producing effective foam suitable for extinguishing an oil fire, at the
rate of at least 90 m3/hr (3180 ft3/hr). A total of at least eight portable tanks of foam-making liquid
are to be supplied on board. In instances where, due to the size of the vessel, only one fire hydrant
is required to be fitted, the vessel need only be provided with one portable foam applicator unit.
这段话该怎么理解。。前面要求船上装备2个泡沫灭火器,后面又说考虑到船体的尺寸,允许只装设一个。
这个尺寸又没有个明确的说法,怎么理解?
回复

使用道具 举报

龙船学院
 楼主| 发表于 2012-6-18 22:58 | 显示全部楼层 来自: 中国福建福州
无人解答下?
回复 支持 反对

使用道具 举报

您需要登录后才可以回帖 登录 | 立即注册

本版积分规则

小黑屋|标签|免责声明|龙船社区

GMT+8, 2024-4-28 03:22

Powered by Imarine

Copyright © 2006, 龙船社区

快速回复 返回顶部 返回列表